Calculate the voltage drop of a 120/240-volt, three-wire underground residential service installed with 2 AWG aluminum URD cable if the load is 80 amperes and the one-way length of the underground service conductors is 100 feet.
Correct Answer:
Verified
Q32: Explain why subpanels are often used in
Q33: The service drop for a residential overhead
Q34: Explain what an MLO panel is.
Q35: A(n) _ usually includes a weatherhead, a
Q36: A(n) _ is a surface on which
Q37: The amount of voltage that is needed
Q38: Conduit clamps used to support a service
Q39: A(n) _ is a type of conduit
Q40: A _ is installed over the service
Q42: Explain the purpose of a porcelain standoff