Figures 21-4 and 21-12

-A 100-hp three-phase squirrel-cage induction motor is connected to a 240-volt line. The motor does not contain a NEMA design code. A dual-element time delay fuse is to be used as the short-circuit protective device. Use the accompanying figure to determine the size needed.
A) 350 A
B) 400 A
C) 450 A
D) 500 A
Correct Answer:
Verified
Q5: Figure 21-10 Q6: Figure 21-4 Q7: Figure 21-14 Q8: The size of the short-circuit protective device Q9: All heater sizes are chosen from a Q11: As a general rule the temperature rating Q12: Different tables from the _ (NEC®) are Q13: Starter sizes are rated by motor type, Q14: When the termination temperature rating is not Q15: There are two basic methods for determining Unlock this Answer For Free Now! View this answer and more for free by performing one of the following actions Scan the QR code to install the App and get 2 free unlocks Unlock quizzes for free by uploading documents![]()
![]()
![]()