While troubleshooting a 24-V control circuit consisting of a thermostat, a pressure control, and a contactor coil, the technician reads 24 volts across the thermostat, 0 volts across the pressure control, and 0 volts across the contactor coil. The technician makes the following statements. The following statements are all considered to be true.
A) The transformer is burned out.
B) The thermostat is open.
C) The contactor coil is energized.
Correct Answer:
Verified
Q14: When using a ten-wrap multiplier, the reading
Q15: A 10-wrap amperage multiplier is used with
Q16: If line one of a circuit had
Q17: A 120-V/24-V control transformer has a VA
Q18: An electrical power consuming component _.
A) is
Q20: An example of a power consuming device
Q21: Non-power-consuming, or power-passing, devices are commonly referred
Q22: In a high voltage circuit, is the
Q23: In a residential air conditioning system, how
Q24: What is the amperage capacity of a