Twelve 14 AWG copper conductors with type RHW insulation are to be installed in conduit in an area with an ambient temperature of 110 degrees F (43 degrees C) . What will be the ampacity of these conductors?
A) 4.1 amperes
B) 8.2 amperes
C) 16.4 amperes
D) 32.8 amperes
Correct Answer:
Verified
Q2: If conductors are to be used in
Q3: What is the maximum operating temperature (in
Q4: An aluminum wire 2250 feet long cannot
Q5: According to the NEC, what five conditions
Q6: After the conductors have been installed in
Q8: If you have a raceway with 35
Q9: Find the resistance of 6 AWG copper
Q10: _loss is caused by the continuous aligning
Q11: The conductors of a single phase are
Q12: Currents of a three-phase system are_ degrees