Consider the Single-Line Diagram of the Power System Shown in Figure

Question 11

Essay

Consider the single-line diagram of the power system shown in Figure P3.11. Equipment rating are:}
 generator 1: 750MVA,18kV,X=0.2 per unit  generator 2: 750MVA,18kV,X=0.2 synchronous motor 3: 1500MVA,20kV,X=0.2 3-phase ΔY transformers T1, T2, T3, T4:750MVA,500kVY/20kVΔ,X=0.1 3-phase Y-Y transformer T5:1500MVA,500kVY/20kVY,X=0.1\begin{array}{ll}\text { generator 1: } & 750 \mathrm{MVA}, 18 \mathrm{kV}, \mathrm{X}^{\prime \prime}=0.2 \text { per unit } \\\text { generator 2: } & 750 \mathrm{MVA}, 18 \mathrm{kV}, \mathrm{X}^{\prime \prime}=0.2 \\\text { synchronous motor 3: } & 1500 \mathrm{MVA}, 20 \mathrm{kV}, \mathrm{X}^{\prime \prime}=0.2 \\\begin{array}{l}\text { 3-phase } \Delta-\mathrm{Y} \text { transformers } \\\mathrm{T}_{1}, \mathrm{~T}_{2}, \mathrm{~T}_{3}, \mathrm{~T}_{4}:\end{array} & 750 \mathrm{MVA}, 500 \mathrm{kV} \mathrm{Y} / 20 \mathrm{kV} \Delta, \mathrm{X}=0.1 \\\text { 3-phase Y-Y transformer } \mathrm{T}_{5}: & 1500 \mathrm{MVA}, 500 \mathrm{kV} \mathrm{Y} / 20 \mathrm{kV} \mathrm{Y}, \mathrm{X}=0.1\end{array}
Neglecting resistance, transformer phase shift, and magnetizing reactance, draw the equivalent reactance diagram. Use a base of 100MVA100 \mathrm{MVA} and 500kV500 \mathrm{kV} for the 40 -ohm line. Determine the per-unit reactances.
 Consider the single-line diagram of the power system shown in Figure P3.11. Equipment rating are:}  \begin{array}{ll} \text { generator 1: } & 750 \mathrm{MVA}, 18 \mathrm{kV}, \mathrm{X}^{\prime \prime}=0.2 \text { per unit } \\ \text { generator 2: } & 750 \mathrm{MVA}, 18 \mathrm{kV}, \mathrm{X}^{\prime \prime}=0.2 \\ \text { synchronous motor 3: } & 1500 \mathrm{MVA}, 20 \mathrm{kV}, \mathrm{X}^{\prime \prime}=0.2 \\ \begin{array}{l} \text { 3-phase } \Delta-\mathrm{Y} \text { transformers } \\ \mathrm{T}_{1}, \mathrm{~T}_{2}, \mathrm{~T}_{3}, \mathrm{~T}_{4}: \end{array} & 750 \mathrm{MVA}, 500 \mathrm{kV} \mathrm{Y} / 20 \mathrm{kV} \Delta, \mathrm{X}=0.1 \\ \text { 3-phase Y-Y transformer } \mathrm{T}_{5}: & 1500 \mathrm{MVA}, 500 \mathrm{kV} \mathrm{Y} / 20 \mathrm{kV} \mathrm{Y}, \mathrm{X}=0.1 \end{array}  Neglecting resistance, transformer phase shift, and magnetizing reactance, draw the equivalent reactance diagram. Use a base of  100 \mathrm{MVA}  and  500 \mathrm{kV}  for the 40 -ohm line. Determine the per-unit reactances.     FIGURE P3.11
FIGURE P3.11

Correct Answer:

verifed

Verified

blured image
Per unit positive sequence r...

View Answer

Unlock this answer now
Get Access to more Verified Answers free of charge

Related Questions

Unlock this Answer For Free Now!

View this answer and more for free by performing one of the following actions

qr-code

Scan the QR code to install the App and get 2 free unlocks

upload documents

Unlock quizzes for free by uploading documents