A Single-Phase Electrical Device in a Building Draws 37 a and Is

Question 12

Multiple Choice

A single-phase electrical device in a building draws 37 A and is supplied with two type THWN copper wires in a conduit. The conduit is run up through the cores of concrete blocks in a building. The wire ampacity is to be sized at 125% of the 37 A, which is 46.25 A. The minimum size of wire permitted is AWG number ____.


A) 4
B) 6
C) 8
D) 10