Single aluminum conductors with type XHHW insulation are mounted overhead on insulators to supply an outbuilding from another building. The 120/240 V, three-wire feeder is protected at the source with a 100 A circuit breaker. The minimum size ungrounded feeder conductors permitted are ____ AWG.
A) 4
B) 6
C) 8
D) 10
Correct Answer:
Verified
Q5: What is the minimum trade size RNC
Q6: "Allowable ampacity" is defined as _.
A) the
Q7: What is the minimum trade size LFMC
Q8: White, or natural gray-colored insulation is _.
A)
Q9: On a three-phase system with voltages greater
Q10: On a three-phase 480/277 V system, the
Q11: What is the minimum trade size RMC
Q12: A single-phase electrical device in a building
Q13: The NEC® requires the high leg of
Q15: Wire type THWN copper is run in