The Ratings of a Three-Phase Three-Winding Transformer Are:
Primary (1) \quad

Question 17

Essay

The ratings of a three-phase three-winding transformer are:
Primary (1): \quad Y connected, 66kV,2066 \mathrm{kV}, 20 MVA
Secondary (2): \quad Y connected, 13.2kV,1513.2 \mathrm{kV}, 15 MVA
Tertiary (3): Δ\quad \Delta connected, 2.3kV,52.3 \mathrm{kV}, 5 MVA
Neglecting winding resistances and exciting current, the per-unit leakage reactances are:
X12=0.08 on a 20MVA,66kV base X13=0.10 on a 20MVA,66kV base X23=0.09 on a 15MVA,13.2kV base \begin{aligned}& \mathrm{X}_{12}=0.08 \text { on a } 20-\mathrm{MVA}, 66-\mathrm{kV} \text { base } \\& \mathrm{X}_{13}=0.10 \text { on a } 20-\mathrm{MVA}, 66-\mathrm{kV} \text { base } \\& \mathrm{X}_{23}=0.09 \text { on a } 15-\mathrm{MVA}, 13.2-\mathrm{kV} \text { base }\end{aligned}
(a) Determine the per-unit reactances X1,X2,X3\mathrm{X}_{1}, \mathrm{X}_{2}, \mathrm{X}_{3} of the equivalent circuit on a 20-MVA, 66kV66-\mathrm{kV} base at the primary terminals. (b) Purely resistive loads of 12MW12 \mathrm{MW} at 13.2kV13.2 \mathrm{kV} and 5MW5 \mathrm{MW} at 2.3kV2.3 \mathrm{kV} are connected to the secondary and tertiary sides of the transformer, respectively. Draw the per-unit impedance diagram, showing the per-unit impedances on a 20MVA,66kV20-\mathrm{MVA}, 66-\mathrm{kV} base at the primary terminals.

Correct Answer:

verifed

Verified

None...

View Answer

Unlock this answer now
Get Access to more Verified Answers free of charge

Related Questions

Unlock this Answer For Free Now!

View this answer and more for free by performing one of the following actions

qr-code

Scan the QR code to install the App and get 2 free unlocks

upload documents

Unlock quizzes for free by uploading documents